Thanks for the tip regarding the levelling systems display panel. I would have thought that since my inside climate controlled storage includes 50 amp plug in (line 1 is 124 volts and line 2 is 121), that this would engage the battery charging system making it unnecessary to disconnect the battery. Question follow-up - Should the Solar system not charge the battery as well? I guess that I can read off the battery voltage from its display panel as well? Would still like to know which line feeds the charge to the battery to check what its charging amperage is coming through at. Thanks again.
If it's sunny and the batteries need charge, the solar should be charging. It's not wired through the disconnect so, if the fuse is good and the chargers are on, it should be working.

There's six pieces of information on the remote:

Top Left: Panel Voltage (should be 25-35v if working)

Top Middle: Amperage supplied by panels (any where from 8.5 to 0 ffrom a single panel)

Top Right: Watts (power provided)

Bottom Left: Output Voltage from Charger (should be slightly higher than actual battery voltage)

Bottom Middle: Amperage to the battery (0-30 may be zero if batteries are full)

Bottom Right: Charger state (OFF, BLK, ABS, FLT, STBY)