Old 12-25-2023, 09:14 AM   #19
pitman44
Seasoned Camper
 
Join Date: Dec 2019
Location: Dryden
Posts: 94
M.O.C. #25471
Quote:
Originally Posted by Bourbon County View Post
Regulator(s) would have to be adjusted or possibly replaced. NG burns at a much lower pressure than LP. An LP appliance is >2X as efficient as NG, in other words a 40K BTU furnace would only be about 20K BTU, same with water heater, cooktop, etc. I would be surprised if the gas company would connect to an RV.
Partially correct. NG operates at 7"wc vs propane at 11"wc. NG has about 1000 btu/cu ft vs propane at about 2500/cu ft. However a furnace that can run on NG or propane has very close to the same output although propane is usually slightly less output than propane. A NG orifice is much larger than a propane orifice in the same appliance.

To answer the OP's question, you would need to change the orifices as well as either install a NG kit or replace the gas valve. My guess is you won't find the necessary components to convert to NG because the demand isn't there to justify the investment. On that point I could be wrong.