Thread: Furnace
View Single Post
Old 03-24-2024, 09:46 AM   #13
jsb5717
Montana Master
 
jsb5717's Avatar
 
Join Date: Mar 2019
Location: Milwaukie, OR
Posts: 1,475
M.O.C. #23668
Quote:
Originally Posted by MandK View Post
Yeah, not sure if it’s the limit switch. My limit switch is in series with the sail switch, if that circuit was interrupted it would not light at all. It would shut down earlier in the sequence of events.
But you can easily test it by the ohm test Chuck suggested or by jumping the 2 blue wires connected to it, essentially bypassing it and keeping the circuit closed. If the furnace runs normally then you can be pretty sure it’s a faulty limit switch. If not, then move on to a different component.

Don’t continue to run the furnace with the limit switch bypassed, though. If faulty, replace immediately.
__________________
Jeff & Sandi (and Teddy - 7lb Schnorkie)
2018 Montana HC 305RL / HW Progressive EMS
2015 RAM 3500 Laramie Longhorn Crew Cab 4x4 DRW / Demco Recon Hitch on RAM Puck Ball
jsb5717 is offline   Reply With Quote