I checked the current NEC and you will need a minimum of 3 conductors, #8 THHN (#6 THHW is adequate). The underground conduit is 1.5” PVC schedule 40. The ground size is #10. I recommend installing an outdoor unfused disconnect ahead and next to the outlet (because of the distance from the panel breaker, an inexpensive plastic HVAC type will do).