Generator neutral-ground bonding
I inadvertently got caught up in a long discussion on another forum about RV generators and bonding neutral to ground. The OP mentioned his Alliance RV showed open ground when on factory installed generator or inverter because neutral was not bonded to ground and asked if that was normal. He said he could not get a clear answer from alliance.
I never had a generator or solar, but with my electrical background I said the GFCI outlets would not function properly without a ground path back to the power source. Several immediately jumped in saying I was wrong because NEC allows GFCI outlets installed in older homes that do not have grounds to the outlets. I tried to explain that old homes and RVs were apples and oranges and can’t be compared.
So this lead to further discussions and me doing quite a bit of research and finding NEC actually has a lengthy section (Article 551) on RV power systems including generators. And has a specific requirement for providing “an effective ground-fault” circuit. OSHA has something similar. And someone else posted a link supporting bonding. The ones who disagreed apparently left the discussion, so I don’t know if I convinced them or simply outlasted them.
So. (Sorry for the long post). My question for you who have generators, both portable and factory installed, is does your generator have neutral to ground bonding? What does Keystone do?
Here is the long discussion if you care to read it.
https://www.rv.net/forum/index.cfm/f...pging/1/page/1
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
06-24-2023, 10:59 AM
|
#2
|
Site Team
Join Date: Oct 2005
Location: Carmichael - CA
Posts: 7,451
M.O.C. #4831
|
I run off either a Honda 2000i or a HF 3500. Neither is grounded. I have a couple of bonded neutral plugs but I usually forget to use them. My Splendide doesn't like either generator and does weird things. I just turn off the breaker., But all my GFCIs work off the generators regardless of the presence or lack on a bonded neutral plug.
Also, I don't use my EMS when running off my generators.
__________________
Carl (n Susan)
There is more to life than fuel mileage.
2012 Montana 3700RL Big Sky Package towed by a 2015 Ford F350 6.7L PSD 4WD CC LWB
|
|
|
06-24-2023, 11:01 AM
|
#3
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,217
M.O.C. #6433
|
I should have said “not trip properly” rather the “not function properly”.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
06-24-2023, 11:17 AM
|
#4
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,217
M.O.C. #6433
|
Another consequence of not bonding would be that if HOT somehow got shorted to RV frame the associated circuit breaker would not trip since with open ground there would be no return path to carry the current. That would leave the frame hot 120 vac.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
06-24-2023, 12:55 PM
|
#5
|
Montana Fan
Join Date: Feb 2022
Location: Cynthiana
Posts: 213
M.O.C. #30449
|
I believe the GFCI receptacle would function properly while running on generator. The GFCI works by measuring the current flow in both the hot and neutral, if the difference is >5 milliamps, it trips, doesn't need a ground reference to measure these currents. The assumption is current is leaking to ground maybe through your body. They are strictly for human protection.
It's understandable that any kind of power protection device would not work, nor would a plug in GFCI tester. The test button on the receptacle should work if you want to test.
That is an interesting point about current leakage to the RV chassis. The truth is unless you're touching the frame or maybe the hitch, there aren't that many conductive surfaces you could touch. The water lines are PEX, drains are ABS. How about those folks pulling Airstreams though!
|
|
|
06-24-2023, 12:58 PM
|
#6
|
Montana Master
Join Date: Oct 2004
Location: Salem
Posts: 7,590
M.O.C. #2283
|
Should we have a ground wire from the ground post on the generator to the camper frame if we already have a bonded ground? I think the answer will be yes. I have wired my house and three phase shop but that doesn’t mean I know anything about electricity except ever pee on an electric fence which I did in the dark one time. Yep once was enough to teach me all I really needed to know.
Lynwood
|
|
|
06-24-2023, 12:58 PM
|
#7
|
Montana Fan
Join Date: Dec 2021
Location: Schertz, TX
Posts: 165
M.O.C. #30294
|
I have a 2022. It's my understanding -- understanding only -- that the transfer switch won't engage unless the RV is neutral - ground bonded and the power source, including generator, is also bonded. My Southwire SurgeGuard 34950 will also indicate a fault if the trailer isn't bonded (open neutral shows on the display). I keep a self-made bonding plug in my Predator 3500 generator and actually use the SurgeGuard when I'm running on generator power as an added level of safety for inadvertent brownouts in case the generator quits or runs out of gas.
__________________
Clark & Peggy
2022 Montana 3791RD, 800i solar, 2x100ah Battleborn
2017 Ford F350, CC, LB, 6.7, 4x4
|
|
|
06-24-2023, 01:47 PM
|
#8
|
Montana Master
Join Date: Mar 2021
Location: Western NY
Posts: 511
M.O.C. #28430
|
I made up a grounding plug for my little 2500 Champion. Everything seems to work as it should, but I just use it to run the charger/converter for the very rare occasions that we are overnighting somewhere without power or when there is a power outage, which seems to be more often than it should be at NY State parks.
__________________
Mark & Karen
2021 3121rl - slide toppers, cottage white, TST 507 TPMS, X-Factors, disc brakes
2021 F-350, 6.7L, SRW CC LB - B&W Companion, Bakflip cover
|
|
|
06-24-2023, 02:06 PM
|
#9
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,217
M.O.C. #6433
|
Quote:
Originally Posted by Bourbon County
I believe the GFCI receptacle would function properly while running on generator. The GFCI works by measuring the current flow in both the hot and neutral, if the difference is >5 milliamps, it trips, doesn't need a ground reference to measure these currents. The assumption is current is leaking to ground maybe through your body. They are strictly for human protection.
…….
|
And that was a large part of the discussion. But for there to be a difference between the amount of current flowing in the hot pin and the amount of current flowing back out the neutral pin requires that the difference has to have “leaked” out of the circuit between the two. But current can’t leak out without a path back to the source, in this case the generator. And with no ground there is no path for that errant ground fault current to get back. So a difference can’t exist. Current must have a closed path back to the initial source to flow.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
06-24-2023, 02:53 PM
|
#10
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,217
M.O.C. #6433
|
Quote:
Originally Posted by mlh
Should we have a ground wire from the ground post on the generator to the camper frame if we already have a bonded ground? I think the answer will be yes. I have wired my house and three phase shop but that doesn’t mean I know anything about electricity except ever pee on an electric fence which I did in the dark one time. Yep once was enough to teach me all I really needed to know.
Lynwood
|
If the NEU and GND are bonded at the source (generator in this case) then frame is connected to NEU thru the ground wire in the power cord when plugged into the generator. No extra wire needed.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
06-24-2023, 05:31 PM
|
#11
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,217
M.O.C. #6433
|
Here is a good description on why NEU-GND bonding is necessary to make GFCIs trip on a ground fault and to keep the “hot frame” condition I mentioned above from occurring.
https://www.rvtravel.com/rv-electric...ng_generators/
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
06-24-2023, 07:57 PM
|
#12
|
Montana Master
Join Date: May 2019
Location: Alton
Posts: 2,759
M.O.C. #24086
|
My Harbor Freight Predator 2000W generator does not have a neutral to ground bond.
I do not have a N-G bonding plug.
Everything works fine.
Spent 10 days dry camping at Moab.
I MAY have a "hot skin" condition on generator/solar power. OR it could have been the dry desert air and static electricity. I will be investigating thoroughly in a few weeks when we are dry camping again.
No "hot skin" (or static electricity) when on Shore power.
__________________
Daryl and Marianne,
2019 3130re 20th Anniversary Edition
2016 F350 Lariat
|
|
|
06-25-2023, 06:32 AM
|
#13
|
Montana Master
Join Date: Oct 2017
Location: Bastrop
Posts: 2,892
M.O.C. #20753
|
Quote:
Originally Posted by Daryles
My Harbor Freight Predator 2000W generator does not have a neutral to ground bond.
I do not have a N-G bonding plug.
Everything works fine.
Spent 10 days dry camping at Moab.
I MAY have a "hot skin" condition on generator/solar power. OR it could have been the dry desert air and static electricity. I will be investigating thoroughly in a few weeks when we are dry camping again.
No "hot skin" (or static electricity) when on Shore power.
|
Hot Skin on genny and not on Shore power. You are prime for a Lynwood electric fence experience.
__________________
Mocha, one-eyed toothless, hurricane survivor, Pirate dog
2019 20th Anniversary Edition 3701LK
B&W 20K for Ford OEM Puck
2018 Ford F-350 Lariat CCLB PSD DRW KJ5CQH
|
|
|
06-25-2023, 07:57 AM
|
#14
|
Montana Master
Join Date: Oct 2004
Location: Salem
Posts: 7,590
M.O.C. #2283
|
Quote:
Originally Posted by jeffba
Hot Skin on genny and not on Shore power. You are prime for a Lynwood electric fence experience.
|
Well not quite. Electric fence is low amp 20,000 voltage camper is 120 but it will still get your attention.
Lynwood
|
|
|
06-25-2023, 08:11 AM
|
#15
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,217
M.O.C. #6433
|
Saw an interesting video of 4 fools standing side by side next to an electric fence. The first 3 were standing on plastic buckets. The last one standing on the ground. The first person grabbed the electric fence and nothing happened. That person held hands with the second person and nothing happened. That person held hands with the third person and nothing happened. As soon as that person touched hands with the fool on the ground they all got shocked.
But that describes the open ground issue. The electric fence controller has a positive terminal connected to the wire and a negative terminal connected to a rod driven into the ground for earth ground. If whatever touches the live wire is not touching the ground source, then nothing happens.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
06-25-2023, 06:35 PM
|
#16
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,217
M.O.C. #6433
|
I am still curious about those who have permanent generators factory installed or dealer installed. Do those have an N-G bond?
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
06-26-2023, 01:00 PM
|
#17
|
Montana Master
Join Date: Oct 2004
Location: Salem
Posts: 7,590
M.O.C. #2283
|
Several years ago I talked to a guy who worked on 760,000 volt transmission lines. He worked from a helicopter. As well as I remember he said he would hook a grounding line from the helicopter to the line and I think he was grounded to the chopper. Then he could work on the bare line without any protection. He did say he had placed on him without any pigment. I don’t know if that came from the high voltage or not. The electricity had no place to go so he was safe.
Lynwood
|
|
|
06-26-2023, 04:43 PM
|
#18
|
Montana Master
Join Date: Oct 2012
Location: Box Elder
Posts: 4,733
M.O.C. #12947
|
Working on any voltage like that isn’t being grounded but having the line and the helicopter connected with the jumper brings everything to the same potential. This is just like a bird landing on the line. Lineman can also work out of an insulated lift bare handed on high voltages too. I never got to do that but did work on high voltages with rubber gloves.
__________________
Bob & Becky
2012 3402RL
2012 Chevy 2500HD D/A CC 4WD
|
|
|
06-26-2023, 05:57 PM
|
#19
|
Montana Master
Join Date: Oct 2006
Location: McKinney
Posts: 7,217
M.O.C. #6433
|
Current passing thru a wire creates an electromagnetic field (EMF) around that wire. The greater the current the stronger the field. And that EMF can create a voltage potential on any adjacent metal close enough. That is the working principle of a transformer. A basic transformer has two wire windings that are not electrically connected to each other. Applying a voltage to the primary winding causes current to flow thru that winding. That current creates an EMF around that wire winding. That EMF causes a potential voltage on the secondary winding. And if something is connected to that secondary winding, current will flow thru it.
I suspect a helicopter that near a high voltage line carrying a lot of current could actually develop a potential voltage on the metal frame of the helicopter. Connecting a wire between the helicopter and the power line ensures that potential voltage doesn’t develop.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
|
|
|
06-26-2023, 06:15 PM
|
#20
|
Montana Master
Join Date: Oct 2004
Location: Salem
Posts: 7,590
M.O.C. #2283
|
Quote:
Originally Posted by BB_TX
Current passing thru a wire creates an electromagnetic field (EMF) around that wire. The greater the current the stronger the field. And that EMF can create a voltage potential on any adjacent metal close enough. That is the working principle of a transformer. A basic transformer has two wire windings that are not electrically connected to each other. Applying a voltage to the primary winding causes current to flow thru that winding. That current creates an EMF around that wire winding. That EMF causes a potential voltage on the secondary winding. And if something is connected to that secondary winding, current will flow thru it.
I suspect a helicopter that near a high voltage line carrying a lot of current could actually develop a potential voltage on the metal frame of the helicopter. Connecting a wire between the helicopter and the power line ensures that potential voltage doesn’t develop.
|
Thanks Bill. That sounds reasonable.