Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
 

Go Back   Montana Owners Club - Keystone Montana 5th Wheel Forum > MOC Technical Forums > Solar, Charging Systems, Batteries and Electrical
Click Here to Login

Reply
 
Thread Tools Search this Thread Display Modes
 
Old 06-24-2023, 10:44 AM   #1
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,203
M.O.C. #6433
Generator neutral-ground bonding

I inadvertently got caught up in a long discussion on another forum about RV generators and bonding neutral to ground. The OP mentioned his Alliance RV showed open ground when on factory installed generator or inverter because neutral was not bonded to ground and asked if that was normal. He said he could not get a clear answer from alliance.

I never had a generator or solar, but with my electrical background I said the GFCI outlets would not function properly without a ground path back to the power source. Several immediately jumped in saying I was wrong because NEC allows GFCI outlets installed in older homes that do not have grounds to the outlets. I tried to explain that old homes and RVs were apples and oranges and can’t be compared.

So this lead to further discussions and me doing quite a bit of research and finding NEC actually has a lengthy section (Article 551) on RV power systems including generators. And has a specific requirement for providing “an effective ground-fault” circuit. OSHA has something similar. And someone else posted a link supporting bonding. The ones who disagreed apparently left the discussion, so I don’t know if I convinced them or simply outlasted them.

So. (Sorry for the long post). My question for you who have generators, both portable and factory installed, is does your generator have neutral to ground bonding? What does Keystone do?

Here is the long discussion if you care to read it.
https://www.rv.net/forum/index.cfm/f...pging/1/page/1
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-24-2023, 10:59 AM   #2
Carl n Susan
Site Team
 
Carl n Susan's Avatar
 
Join Date: Oct 2005
Location: Carmichael - CA
Posts: 7,429
M.O.C. #4831
I run off either a Honda 2000i or a HF 3500. Neither is grounded. I have a couple of bonded neutral plugs but I usually forget to use them. My Splendide doesn't like either generator and does weird things. I just turn off the breaker., But all my GFCIs work off the generators regardless of the presence or lack on a bonded neutral plug.

Also, I don't use my EMS when running off my generators.
__________________
Carl (n Susan)
There is more to life than fuel mileage.
2012 Montana 3700RL Big Sky Package towed by a 2015 Ford F350 6.7L PSD 4WD CC LWB

Carl n Susan is offline   Reply With Quote
Old 06-24-2023, 11:01 AM   #3
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,203
M.O.C. #6433
I should have said “not trip properly” rather the “not function properly”.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-24-2023, 11:17 AM   #4
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,203
M.O.C. #6433
Another consequence of not bonding would be that if HOT somehow got shorted to RV frame the associated circuit breaker would not trip since with open ground there would be no return path to carry the current. That would leave the frame hot 120 vac.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-24-2023, 12:58 PM   #5
C&P RV
Montana Fan
 
C&P RV's Avatar
 
Join Date: Dec 2021
Location: Schertz, TX
Posts: 163
M.O.C. #30294
I have a 2022. It's my understanding -- understanding only -- that the transfer switch won't engage unless the RV is neutral - ground bonded and the power source, including generator, is also bonded. My Southwire SurgeGuard 34950 will also indicate a fault if the trailer isn't bonded (open neutral shows on the display). I keep a self-made bonding plug in my Predator 3500 generator and actually use the SurgeGuard when I'm running on generator power as an added level of safety for inadvertent brownouts in case the generator quits or runs out of gas.
__________________
Clark & Peggy
2022 Montana 3791RD, 800i solar, 2x100ah Battleborn
2017 Ford F350, CC, LB, 6.7, 4x4
C&P RV is offline   Reply With Quote
Old 06-24-2023, 12:55 PM   #6
Bourbon County
Montana Fan
 
Join Date: Feb 2022
Location: Cynthiana
Posts: 211
M.O.C. #30449
I believe the GFCI receptacle would function properly while running on generator. The GFCI works by measuring the current flow in both the hot and neutral, if the difference is >5 milliamps, it trips, doesn't need a ground reference to measure these currents. The assumption is current is leaking to ground maybe through your body. They are strictly for human protection.

It's understandable that any kind of power protection device would not work, nor would a plug in GFCI tester. The test button on the receptacle should work if you want to test.

That is an interesting point about current leakage to the RV chassis. The truth is unless you're touching the frame or maybe the hitch, there aren't that many conductive surfaces you could touch. The water lines are PEX, drains are ABS. How about those folks pulling Airstreams though!
Bourbon County is offline   Reply With Quote
Old 06-24-2023, 02:06 PM   #7
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,203
M.O.C. #6433
Quote:
Originally Posted by Bourbon County View Post
I believe the GFCI receptacle would function properly while running on generator. The GFCI works by measuring the current flow in both the hot and neutral, if the difference is >5 milliamps, it trips, doesn't need a ground reference to measure these currents. The assumption is current is leaking to ground maybe through your body. They are strictly for human protection.
…….
And that was a large part of the discussion. But for there to be a difference between the amount of current flowing in the hot pin and the amount of current flowing back out the neutral pin requires that the difference has to have “leaked” out of the circuit between the two. But current can’t leak out without a path back to the source, in this case the generator. And with no ground there is no path for that errant ground fault current to get back. So a difference can’t exist. Current must have a closed path back to the initial source to flow.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-28-2023, 06:12 PM   #8
firestation12
Montana Fan
 
Join Date: Jul 2019
Location: Mesa
Posts: 280
M.O.C. #24588
Quote:
Originally Posted by BB_TX View Post
And that was a large part of the discussion. But for there to be a difference between the amount of current flowing in the hot pin and the amount of current flowing back out the neutral pin requires that the difference has to have “leaked” out of the circuit between the two. But current can’t leak out without a path back to the source, in this case the generator. And with no ground there is no path for that errant ground fault current to get back. So a difference can’t exist. Current must have a closed path back to the initial source to flow.
I’ve read this post several times in an effort to fully understand the terminology BB_TX is using or how the point being made is valid. For starters, I disagree with the above quoted statement in it’s totality. There seems to be a misunderstanding of the function of a GFCI and a circuit breaker. Current can “leak out” of a hot conductor without a return pathway to the generator, shore power, or whatever source. Overcurrent devices (breakers), AFCIs and GFCI’s handle dangerous electrical voltage in several different but key ways. Circuit breakers can be manufactured to perform more than one function i.e. open a circuit instantaneously in the case of a direct short circuit, open when current flow would cause wiring to overheat over time, open a circuit with the presence of arcing, and opening a circuit with detection of minute current losses capable of producing death but not enough to open a circuit with a full short to neutral or ground. Single purpose protection devices are found in our campers… GFCIs and circuit breakers. Circuit beakers require a clear pathway back to the neutral or ground to perform their intended function. A GFCI does not. I’m in agreement with post #5, i.e. a GFCI operates properly with or without a ground. It only monitors the relationship of the hot to neutral. Any discrepancy between the two causes a trip. Remove the ground wire from the GFCI and it still functions normally. The GFCI has no idea from what source power is being supplied… generator (with or without a neutral/ground jumper), shore power or inverter. The use of GFCI circuit breakers has long been a workaround fix for older homes that lacked grounded receptacles. The inexpensive 3 light (2 yellow and one red) plug in GFCI tester that many of those here on the forum have and use, DOES rely on a properly grounded GFCI outlet to create a leak pathway when the test button is pushed. IF…. a generator were to incorporate a GFCI as its primary source to an un-bonded camper, the GFCI would trip when the “hot” skin was touched whether or not the generator was bonded to the camper frame. The ground wire on the GFCI is there simply to provide a pathway for the circuit breaker to trip. GFCI outlets do not provide short circuit protection.
firestation12 is offline   Reply With Quote
Old 06-28-2023, 07:15 PM   #9
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,203
M.O.C. #6433
Quote:
Originally Posted by firestation12 View Post
I’ve read this post several times in an effort to fully understand the terminology BB_TX is using or how the point being made is valid. For starters, I disagree with the above quoted statement in it’s totality. There seems to be a misunderstanding of the function of a GFCI and a circuit breaker. Current can “leak out” of a hot conductor without a return pathway to the generator, shore power, or whatever source. ………….
A very basic principle of electricity is that there must be a closed circuit to provide a path for current (electrons) to flow from the positive terminal of the power source to the negative terminal of that same power source. What goes out comes back in. Those electrons can not “leak” out without a path back to that power source. That defies that basic principle. You feel otherwise so please show me some technical source that validates your statement that it is possible. I would really like to know if that is in fact possible.

And yes I fully understand GFCI outlet. Yes, a GFCI outlet with no ground will supply power to the appliance plugged into it. No, the GFCI will not trip on a ground fault without some path back to the power source for the leakage current to travel to create the necessary imbalance. Those electrons can not leak into thin air.

NEC permits the use of GFCIs in older homes with no ground wiring. GFCIs are required in areas that may be exposed to wet conditions such as around sinks and faucets. Water in older homes comes from buried pipes. Pipes buried in the ground become earth ground just as a ground rod driven into the ground would. This provides the return path for a GFCI in an older home with no wired ground to trip on a ground fault.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-29-2023, 09:24 AM   #10
firestation12
Montana Fan
 
Join Date: Jul 2019
Location: Mesa
Posts: 280
M.O.C. #24588
Quote:
Originally Posted by BB_TX View Post
A very basic principle of electricity is that there must be a closed circuit to provide a path for current (electrons) to flow from the positive terminal of the power source to the negative terminal of that same power source. What goes out comes back in. Those electrons can not “leak” out without a path back to that power source. That defies that basic principle. You feel otherwise so please show me some technical source that validates your statement that it is possible. I would really like to know if that is in fact possible.

And yes I fully understand GFCI outlet. Yes, a GFCI outlet with no ground will supply power to the appliance plugged into it. No, the GFCI will not trip on a ground fault without some path back to the power source for the leakage current to travel to create the necessary imbalance. Those electrons can not leak into thin air.

NEC permits the use of GFCIs in older homes with no ground wiring. GFCIs are required in areas that may be exposed to wet conditions such as around sinks and faucets. Water in older homes comes from buried pipes. Pipes buried in the ground become earth ground just as a ground rod driven into the ground would. This provides the return path for a GFCI in an older home with no wired ground to trip on a ground fault.
A GFCI certainly will perform its intended function without a grounding conductor attached. It needs only a hot and neutral to function. Perform a search, “will a GFCI trip without a ground?”. I did love the hokey explanation how old galvanized piping is what allows a GFCI without a ground to function. You probably are not aware that that a circuit breaker style GFCI will trip even if the neutral is lost somewhere between a downstream outlet and the panel. Why? The small curly white pigtail of the CFCI circuit breaker is the source of monitoring the imbalance of the hot and neutral. Of course nothing plugged into the outlet will work, but the shock protection is still functional. Here’s another statement that befuddles,
“Those electrons can not “leak” out without a path back to that power source. That defies that basic principle”. A current leakage can occur anyplace a grounding fault takes place. You seem to imply there has to be a dedicated pathway going directly to the power source for a leak to occur. Am I mis-quoting you? As for your request to provide any sources to validate my claim, I’d prefer you validate my claim. Place a generator on an isolating surface, start it, remove shoes, insert a screw driver firmly into the smaller vertical opening of a receptacle, finally without touching the generator grab the bare metal screw driver shaft. Report back if a dedicated path back to the generator (power source) is necessary for a leak to occur. Lastly I’ll pass on the discussion of positive/negative poles on alternating current. I’ve been unable find a way to make my Fieldpiece meter show that, when I switch the probes between hot and neutral wires. I hesitate to use the DC setting to see if that can sense pos/neg.
firestation12 is offline   Reply With Quote
Old 06-24-2023, 12:58 PM   #11
mlh
Montana Master
 
Join Date: Oct 2004
Location: Salem
Posts: 7,573
M.O.C. #2283
Should we have a ground wire from the ground post on the generator to the camper frame if we already have a bonded ground? I think the answer will be yes. I have wired my house and three phase shop but that doesn’t mean I know anything about electricity except ever pee on an electric fence which I did in the dark one time. Yep once was enough to teach me all I really needed to know.
Lynwood
__________________
www.harrellsprec.com
Lynwood Harrell
323 RL HC 2008 F250
mlh is offline   Reply With Quote
Old 06-24-2023, 02:53 PM   #12
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,203
M.O.C. #6433
Quote:
Originally Posted by mlh View Post
Should we have a ground wire from the ground post on the generator to the camper frame if we already have a bonded ground? I think the answer will be yes. I have wired my house and three phase shop but that doesn’t mean I know anything about electricity except ever pee on an electric fence which I did in the dark one time. Yep once was enough to teach me all I really needed to know.
Lynwood
If the NEU and GND are bonded at the source (generator in this case) then frame is connected to NEU thru the ground wire in the power cord when plugged into the generator. No extra wire needed.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-24-2023, 01:47 PM   #13
MandK
Montana Fan
 
Join Date: Mar 2021
Location: Western NY
Posts: 498
M.O.C. #28430
I made up a grounding plug for my little 2500 Champion. Everything seems to work as it should, but I just use it to run the charger/converter for the very rare occasions that we are overnighting somewhere without power or when there is a power outage, which seems to be more often than it should be at NY State parks.
__________________
Mark & Karen
2021 3121rl - slide toppers, cottage white, TST 507 TPMS, X-Factors, disc brakes
2021 F-350, 6.7L, SRW CC LB - B&W Companion, Bakflip cover
MandK is offline   Reply With Quote
Old 06-24-2023, 05:31 PM   #14
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,203
M.O.C. #6433
Here is a good description on why NEU-GND bonding is necessary to make GFCIs trip on a ground fault and to keep the “hot frame” condition I mentioned above from occurring.

https://www.rvtravel.com/rv-electric...ng_generators/
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-24-2023, 07:57 PM   #15
Daryles
Montana Master
 
Daryles's Avatar
 
Join Date: May 2019
Location: Alton
Posts: 2,738
M.O.C. #24086
My Harbor Freight Predator 2000W generator does not have a neutral to ground bond.
I do not have a N-G bonding plug.
Everything works fine.
Spent 10 days dry camping at Moab.
I MAY have a "hot skin" condition on generator/solar power. OR it could have been the dry desert air and static electricity. I will be investigating thoroughly in a few weeks when we are dry camping again.
No "hot skin" (or static electricity) when on Shore power.
__________________
Daryl and Marianne,
2019 3130re 20th Anniversary Edition
2016 F350 Lariat
Daryles is offline   Reply With Quote
Old 06-25-2023, 06:32 AM   #16
jeffba
Montana Master
 
Join Date: Oct 2017
Location: Bastrop
Posts: 2,892
M.O.C. #20753
Quote:
Originally Posted by Daryles View Post
My Harbor Freight Predator 2000W generator does not have a neutral to ground bond.
I do not have a N-G bonding plug.
Everything works fine.
Spent 10 days dry camping at Moab.
I MAY have a "hot skin" condition on generator/solar power. OR it could have been the dry desert air and static electricity. I will be investigating thoroughly in a few weeks when we are dry camping again.
No "hot skin" (or static electricity) when on Shore power.
Hot Skin on genny and not on Shore power. You are prime for a Lynwood electric fence experience.
__________________
Mocha, one-eyed toothless, hurricane survivor, Pirate dog
2019 20th Anniversary Edition 3701LK
B&W 20K for Ford OEM Puck
2018 Ford F-350 Lariat CCLB PSD DRW KJ5CQH
jeffba is offline   Reply With Quote
Old 06-25-2023, 07:57 AM   #17
mlh
Montana Master
 
Join Date: Oct 2004
Location: Salem
Posts: 7,573
M.O.C. #2283
Quote:
Originally Posted by jeffba View Post
Hot Skin on genny and not on Shore power. You are prime for a Lynwood electric fence experience.

Well not quite. Electric fence is low amp 20,000 voltage camper is 120 but it will still get your attention.
Lynwood
__________________
www.harrellsprec.com
Lynwood Harrell
323 RL HC 2008 F250
mlh is offline   Reply With Quote
Old 06-25-2023, 08:11 AM   #18
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,203
M.O.C. #6433
Saw an interesting video of 4 fools standing side by side next to an electric fence. The first 3 were standing on plastic buckets. The last one standing on the ground. The first person grabbed the electric fence and nothing happened. That person held hands with the second person and nothing happened. That person held hands with the third person and nothing happened. As soon as that person touched hands with the fool on the ground they all got shocked.

But that describes the open ground issue. The electric fence controller has a positive terminal connected to the wire and a negative terminal connected to a rod driven into the ground for earth ground. If whatever touches the live wire is not touching the ground source, then nothing happens.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-25-2023, 06:35 PM   #19
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,203
M.O.C. #6433
I am still curious about those who have permanent generators factory installed or dealer installed. Do those have an N-G bond?
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 06-26-2023, 01:00 PM   #20
mlh
Montana Master
 
Join Date: Oct 2004
Location: Salem
Posts: 7,573
M.O.C. #2283
Several years ago I talked to a guy who worked on 760,000 volt transmission lines. He worked from a helicopter. As well as I remember he said he would hook a grounding line from the helicopter to the line and I think he was grounded to the chopper. Then he could work on the bare line without any protection. He did say he had placed on him without any pigment. I don’t know if that came from the high voltage or not. The electricity had no place to go so he was safe.
Lynwood
__________________
www.harrellsprec.com
Lynwood Harrell
323 RL HC 2008 F250
mlh is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 03:05 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.