05-18-2022, 05:31 PM
|
#1
|
New Member
Join Date: May 2022
Location: Eugene
Posts: 7
M.O.C. #31015
|
Heat pump not working right after "service"
We purchased our barely used 2021 3781 last spring and it has been great. The only issue that we had was the furnace exhaust was ridiculously resonate. This wasn't an issue as the heat pump in electric mode worked great and we just used that. We took the trailer back to the dealer for some pre agreed repairs and mentioned the exhaust to them. They said they could look at it. Well they did make the furnace better by "tuning" the exhaust a bit. BUT... Our system will only run in furnace mode now. Even with outside temp showing in the 60s the furnace will kick on when electric heat is selected and nothing we do with controls will get only the heat pump to operate as it did before. I have taken it back to the dealer a couple times and gotten the same shoulder shrug. I assume that when the furnace was worked on the tech jumpered the furnace and did not remove that jumper but damned if I can find it. Any ideas of how to get the heat pump working properly again??
|
|
|
05-19-2022, 08:20 AM
|
#2
|
Montana Master
Join Date: Aug 2015
Location: Mena
Posts: 504
M.O.C. #17723
|
When the heat system is working properly, The heat pump and heater will work together.
When you have heat set to electric, and the Set temp on the thermostat is >3 degrees above the temp at the sensor (ambient temp), then both heat pump AND heater will come on.
Is your rig a Legacy model and have In-Command?
There may be some 'special' settings I can help you with for gas only heat.
__________________
Ron & Rhonda
2021 3230CK Montana Legacy w/ Super SolarFlex
(old rig) 2015 Montana 3611RL 8K I.S., Disk Brakes, Sailun Tires
2015 F350 XLT Crew Dually 20K B&W Companion
|
|
|
05-19-2022, 08:26 AM
|
#3
|
New Member
Join Date: May 2022
Location: Eugene
Posts: 7
M.O.C. #31015
|
We do have the in command system. I have tried binging the set temp up one degree at a time in electric mode and the furnace still kicks on. I don't recall having the issue prior to the furnace work.
Thank you in advance
|
|
|
05-19-2022, 08:29 AM
|
#4
|
Montana Master
Join Date: Aug 2015
Location: Mena
Posts: 504
M.O.C. #17723
|
OK. what is the Fan setting on when you have tried the heater?
__________________
Ron & Rhonda
2021 3230CK Montana Legacy w/ Super SolarFlex
(old rig) 2015 Montana 3611RL 8K I.S., Disk Brakes, Sailun Tires
2015 F350 XLT Crew Dually 20K B&W Companion
|
|
|
05-19-2022, 08:37 AM
|
#5
|
Montana Master
Join Date: Aug 2015
Location: Mena
Posts: 504
M.O.C. #17723
|
another test:
Mode = Heat
Source = Gas
Fan = Off
This should turn on furnace without heat pump fan.
__________________
Ron & Rhonda
2021 3230CK Montana Legacy w/ Super SolarFlex
(old rig) 2015 Montana 3611RL 8K I.S., Disk Brakes, Sailun Tires
2015 F350 XLT Crew Dually 20K B&W Companion
|
|
|
05-19-2022, 09:25 AM
|
#6
|
Montana Master
Join Date: Mar 2019
Location: Milwaukie, OR
Posts: 1,485
M.O.C. #23668
|
Just for fun I would be temped to take the furnace out of the mix to see if you can get the heat pump to engage. You can turn it off at the control board or pull the fuse. That might tell you something. Also, which thermostat do you have? Some of the Dometics can be finiky or glitchy.
__________________
Jeff & Sandi (and Teddy - 7lb Schnorkie)
2018 Montana HC 305RL / HW Progressive EMS
2015 RAM 3500 Laramie Longhorn Crew Cab 4x4 DRW / Demco Recon Hitch on RAM Puck Ball
|
|
|
05-19-2022, 10:54 AM
|
#7
|
Montana Master
Join Date: Aug 2015
Location: Mena
Posts: 504
M.O.C. #17723
|
Here are some pictures of my heater wiring.
ASA Electronics are the ones to talk to about In-Command, AC/Heat pump operation.
(800)688-3135
One other option: (after verifying wiring)
Re Boot the whole system. Sometime it will get confused.
Disconnect AC power, remove batteries (either switch or Neg. battery post.)
Reconnect.
__________________
Ron & Rhonda
2021 3230CK Montana Legacy w/ Super SolarFlex
(old rig) 2015 Montana 3611RL 8K I.S., Disk Brakes, Sailun Tires
2015 F350 XLT Crew Dually 20K B&W Companion
|
|
|
05-19-2022, 11:01 AM
|
#8
|
Montana Master
Join Date: Aug 2015
Location: Mena
Posts: 504
M.O.C. #17723
|
Download the "MyKeystone" app.
Here: https://www.keystonerv.com/mykeystone
Also, manuals and troubleshooting guides here:
https://www.keystonerv.com/owners-manuals
__________________
Ron & Rhonda
2021 3230CK Montana Legacy w/ Super SolarFlex
(old rig) 2015 Montana 3611RL 8K I.S., Disk Brakes, Sailun Tires
2015 F350 XLT Crew Dually 20K B&W Companion
|
|
|
05-23-2022, 04:47 PM
|
#9
|
Established Member
Join Date: May 2020
Location: Hampton bays
Posts: 16
M.O.C. #26229
|
Heat Pump
So it took 2 years and alot of letters to finally get the heat pump problem fixed,
we went thru, its too cold its too hot, ect...... so finally the AC with a heat pump is not in the living room it is in the Bedroom, and was not wired to any of the thermostats.
it will be wired to the bedroom thermostat. We will see if it works when we get the unit back. I have Keystone CS and Camping world CS and Service working this issue. It should not have left the factory installed incorrectly.
|
|
|
05-24-2022, 06:25 AM
|
#10
|
Montana Master
Join Date: Dec 2017
Location: Mountain Home
Posts: 848
M.O.C. #20949
|
If the thermostats are wired using a CANBUS then the HP should have been on the largest zone.. typically the LR and the two blue signal wires for the furnace should be on the zone 1 roof AC control board and run down to furnace control board.
If the unit is using one thermostat or In Command to control HVAC operation then a CANBUS is in use...
If there are two separate thermostats then CANBUS is not being used
|
|
|
05-25-2022, 01:16 PM
|
#11
|
Montana Master
Join Date: Aug 2004
Location: Livermore
Posts: 5,159
M.O.C. #1920
|
AA Ron, did you get your heat pump working again?
__________________
Ron and Terrie Ames - MOC #1920/KF0NTA
2021Montana 3230CK Super Solar Legacy Package
2021 Ram 3500 Laramie Longhorn, BIM Charging
4x4, SRW, LB, Crew Cab, Pullrite 3900 Hitch
|
|
|
05-25-2022, 06:27 PM
|
#12
|
Seasoned Camper
Join Date: Jul 2020
Location: Franktown
Posts: 51
M.O.C. #26693
|
Heat pump / furnace
We have a 21 legacy 3120 and experienced similar but not exact issue. Suggest change out the 15 amp fuse that is auto reset with a standard fuse. This solved the problem for us.
Best of luck!
|
|
|
05-26-2022, 09:58 AM
|
#13
|
New Member
Join Date: May 2022
Location: Eugene
Posts: 7
M.O.C. #31015
|
Thank you all for good information.
Will be digging into this over the weekend. Will update
|
|
|
05-26-2022, 10:20 AM
|
#14
|
New Member
Join Date: May 2022
Location: Eugene
Posts: 7
M.O.C. #31015
|
Quote:
Originally Posted by rames14
AA Ron, did you get your heat pump working again?
|
going at it this weekend
|
|
|
05-26-2022, 10:21 AM
|
#15
|
New Member
Join Date: May 2022
Location: Eugene
Posts: 7
M.O.C. #31015
|
Quote:
Originally Posted by Arkware
Here are some pictures of my heater wiring.
ASA Electronics are the ones to talk to about In-Command, AC/Heat pump operation.
(800)688-3135
One other option: (after verifying wiring)
Re Boot the whole system. Sometime it will get confused.
Disconnect AC power, remove batteries (either switch or Neg. battery post.)
Reconnect.
|
thank you for the pics. these will help alot
|
|
|
|