Lithium. Batteries

I have 6 100Ah Battle born batteries connected in parallel. I would like to get 2 more with a total of 800 Ah battery bank. I am not sure if it is a good idea to have 8 batteries connected in parallel in case one goes bad. Will that affect the others?
Any input would be great.
 
sunshine 1 is offline   Reply With Quote
Old 05-02-2022, 03:28 PM   #2
PNW Fireguy
Montana Master
 
PNW Fireguy's Avatar
 
Join Date: Nov 2015
Location: Arlington
Posts: 1,522
M.O.C. #18081
As long as you don't have thousands of cycles on the existing batteries go ahead and add the two additional BB's. They are self contained batteries so if something goes wrong with one or more the internal BMS is designed to disconnect the battery from the electrical circuit.
__________________
SOB
2015 Volvo VNL780 D13, iShift, 32k ET air hitch, Idle Free LiFePO4 APU
16.8KWhr LiFePO4, 2.52 kw solar, 10kva Victron split phase
PNW Fireguy is offline   Reply With Quote
Old 05-02-2022, 04:33 PM   #3
rames14
Montana Master
 
rames14's Avatar
 
Join Date: Aug 2004
Location: Livermore
Posts: 5,135
M.O.C. #1920
How many watts of solar do you have?
__________________
Ron and Terrie Ames - MOC #1920/KF0NTA
2021Montana 3230CK Super Solar Legacy Package
2021 Ram 3500 Laramie Longhorn, BIM Charging
4x4, SRW, LB, Crew Cab, Pullrite 3900 Hitch
rames14 is offline   Reply With Quote
Old 05-03-2022, 07:35 AM   #4
sunshine 1
Montana Fan
 
Join Date: Oct 2018
Location: Grandview
Posts: 189
M.O.C. #22947
Thanks PNW Fireguy,
I have about 2000 watts of solar.
sunshine 1 is offline   Reply With Quote
Old 05-03-2022, 07:42 AM   #5
rames14
Montana Master
 
rames14's Avatar
 
Join Date: Aug 2004
Location: Livermore
Posts: 5,135
M.O.C. #1920
The reason I asked about your solar is that about 2 x your battery amperage is a good rule of thumb for sizing batteries to panel wattage. If your battery bank is oversized for your panels, they will never get fully charged unless you are topping them off daily some other way. You are fine with 2000 watts for 800 ah of battery. If you had the space and $’s, your solar array could actually handle 4 more batteries.
__________________
Ron and Terrie Ames - MOC #1920/KF0NTA
2021Montana 3230CK Super Solar Legacy Package
2021 Ram 3500 Laramie Longhorn, BIM Charging
4x4, SRW, LB, Crew Cab, Pullrite 3900 Hitch
rames14 is offline   Reply With Quote
Old 05-03-2022, 08:03 PM   #6
jetskier
Montana Fan
 
jetskier's Avatar
 
Join Date: Aug 2018
Location: Minden - NV
Posts: 499
M.O.C. #22360
Since we are on the topic of solar charging a large battery array, what kind of charging efficiency are you folks seeing from your panels? Let's assume a fixed mount system and non-pivoting mounts. Summer months when the sun is overhead. I have just under 1200W of panels. Most of the time (like this time of year), I see 750-850W during mid-day. That's around 66-70%. I run my array in a series/parallel configuration. six panels total, (3 in series and paralleled to controller). It usually puts out 75-80V and 10-15A.

I'm wondering if I'm losing too much from using the tiny factory solar wires even though I'm well under 20A.

I'm contemplating adding a second controller and running heavier wire to the roof and splitting the two sides.
__________________
2013 F350 Lariat Ultimate CC LB
2019 3790RD
jetskier is offline   Reply With Quote
Old 05-04-2022, 07:53 AM   #7
rames14
Montana Master
 
rames14's Avatar
 
Join Date: Aug 2004
Location: Livermore
Posts: 5,135
M.O.C. #1920
I can tell you all of my panels are in Series. That prevents shade on one impacting the others. In January, our 1200 watts were producing about 4.2 kWh per day. We were seeing a charge from about 8-4 pm. So, about 525 watts per hour. As the sun gets more overhead, I would expect to see what you are seeing.

Here is a good Battleborn article. They figure 350 watts/day from a 100 watt panel.
https://battlebornbatteries.com/rv-solar-panels-guide/
__________________
Ron and Terrie Ames - MOC #1920/KF0NTA
2021Montana 3230CK Super Solar Legacy Package
2021 Ram 3500 Laramie Longhorn, BIM Charging
4x4, SRW, LB, Crew Cab, Pullrite 3900 Hitch
rames14 is offline   Reply With Quote
Old 05-04-2022, 08:07 AM   #8
PNW Fireguy
Montana Master
 
PNW Fireguy's Avatar
 
Join Date: Nov 2015
Location: Arlington
Posts: 1,522
M.O.C. #18081
Lot’s to digest here however your PV output based upon the time of year and your stated parameters is not way off mean numbers. If your roof is curved and you have both parallel strings on the same SCC this could effect the MPPT for the SCC assuming that you are using an MPPT vs PWM SCC. Separating the strings to individual SCC’s will help maximize each strings output. Based again on what info you provided it sounds like you may be using 190watt panels that have an IMP around 9 amps. If that is the case the amperage output from your array is inline. The factory solar wiring at your PV array voltage would be a challenge for me. You can check the voltage output of your array on the roof and then check the voltage at the SCC input to get a idea of your voltage drop. The voltage not the current should be your concern for that wire run. Think of it as the pressure available to push the 14-15A of current from the PV array to the SCC. I have factory installed 10AWG wiring from my roof to the basement but my PV array runs at 150vdc. Any voltage drop is neglible. One more item if your panels have bypass diodes then shading degradation is minimized. Most modern panels have them but you can easily verify by opening the connection box on the back of panel or via the manufacturer spec sheet.

Added some historical data for reference.
Attached Thumbnails
Click image for larger version

Name:	DAC0AA14-3139-4BCD-ABEA-D0DF19D41A32.jpg
Views:	23
Size:	78.9 KB
ID:	11864  
__________________
SOB
2015 Volvo VNL780 D13, iShift, 32k ET air hitch, Idle Free LiFePO4 APU
16.8KWhr LiFePO4, 2.52 kw solar, 10kva Victron split phase
PNW Fireguy is offline   Reply With Quote
Old 05-04-2022, 08:39 AM   #9
scattershot
Montana Master
 
Join Date: Feb 2006
Location: Denver
Posts: 1,041
M.O.C. #5329
2000 w of solar and eight batteries, you could probably run an arc welder with that setup. ;-)
scattershot is offline   Reply With Quote
Old 05-04-2022, 02:09 PM   #10
jetskier
Montana Fan
 
jetskier's Avatar
 
Join Date: Aug 2018
Location: Minden - NV
Posts: 499
M.O.C. #22360
Quote:
Originally Posted by PNW Fireguy View Post
The voltage not the current should be your concern for that wire run. Think of it as the pressure available to push the 14-15A of current from the PV array to the SCC. I have factory installed 10AWG wiring from my roof to the basement but my PV array runs at 150vdc. Any voltage drop is neglible.

I have the Victron 150/85 SCC. I have four 160W panels and two 270W panels. They have the same operating current of 8.77A. I did try to run all six in series, but it over voltaged my controller during that experiment. I do want to run a couple more panels so I think I'll get another controller and split the sides of the roof for each controller. That'll keep me under 150V on each string and the shading from the ACs won't have such a large impact on production during the lower sun angles.
__________________
2013 F350 Lariat Ultimate CC LB
2019 3790RD
jetskier is offline   Reply With Quote
Old 05-04-2022, 03:54 PM   #11
PNW Fireguy
Montana Master
 
PNW Fireguy's Avatar
 
Join Date: Nov 2015
Location: Arlington
Posts: 1,522
M.O.C. #18081
Be sure to take into account temp correction when determining how many panels to put in series. My PV strings total just under 150V without temp correction however dependent upon how cold the weather turns where I am they could potentially put out 187Vdc which would have damaged a 150/100. Over paneling also seems to be the IN thing right now as well. Your controller is plenty big enough for the current. As you stated it's the panel configuration and the resultant array voltage that's limiting. I have the same issue. I have a pair of 250/100 in a 24v system. As per my previous post you will want to make sure that your panels have bypass diodes. They block the shaded panel while keeping the unaffected panel in series output functioning.
__________________
SOB
2015 Volvo VNL780 D13, iShift, 32k ET air hitch, Idle Free LiFePO4 APU
16.8KWhr LiFePO4, 2.52 kw solar, 10kva Victron split phase
PNW Fireguy is offline   Reply With Quote
Old 05-04-2022, 04:12 PM   #12
jetskier
Montana Fan
 
jetskier's Avatar
 
Join Date: Aug 2018
Location: Minden - NV
Posts: 499
M.O.C. #22360
Yep. When I ran that series test, the temps were in the 50's so the panels were kicking out more than the standard published values. I have the diodes.


This is the highest I ever saw for output to the batteries - 68A. It was midday in March last year.
Attached Thumbnails
Click image for larger version

Name:	Solar 954.jpg
Views:	14
Size:	66.9 KB
ID:	11866  
__________________
2013 F350 Lariat Ultimate CC LB
2019 3790RD
jetskier is offline   Reply With Quote
Old 05-08-2022, 02:41 PM   #13
bcrvman
Montana Master
 
Join Date: Jun 2020
Location: Qualicum Beach
Posts: 665
M.O.C. #26399
Quote:
Originally Posted by rames14 View Post
I can tell you all of my panels are in Series. That prevents shade on one impacting the others. In January, our 1200 watts were producing about 4.2 kWh per day. We were seeing a charge from about 8-4 pm. So, about 525 watts per hour. As the sun gets more overhead, I would expect to see what you are seeing.

Here is a good Battleborn article. They figure 350 watts/day from a 100 watt panel.
https://battlebornbatteries.com/rv-solar-panels-guide/
I think you mean in parallel, series connections are affected by shade but not like the old days but they drive an MPPT better.
__________________
2018 Keystone Montana 3811MS
2017 Ford F450 diesel dually
600AH Battle Born Lithium Batteries, 1,080 watts solar
3,000 watt hybrid inverter with 120A charger
bcrvman is offline   Reply With Quote
Old 05-08-2022, 03:00 PM   #14
rames14
Montana Master
 
rames14's Avatar
 
Join Date: Aug 2004
Location: Livermore
Posts: 5,135
M.O.C. #1920
You are correct, Parallel. Senior moment.
__________________
Ron and Terrie Ames - MOC #1920/KF0NTA
2021Montana 3230CK Super Solar Legacy Package
2021 Ram 3500 Laramie Longhorn, BIM Charging
4x4, SRW, LB, Crew Cab, Pullrite 3900 Hitch
rames14 is offline   Reply With Quote
Old 05-08-2022, 06:28 PM   #15
PNW Fireguy
Montana Master
 
PNW Fireguy's Avatar
 
Join Date: Nov 2015
Location: Arlington
Posts: 1,522
M.O.C. #18081
Quote:
Originally Posted by bcrvman View Post
I think you mean in parallel, series connections are affected by shade but not like the old days but they drive an MPPT better.



Yup, bypass diodes make all the difference in the world.
__________________
SOB
2015 Volvo VNL780 D13, iShift, 32k ET air hitch, Idle Free LiFePO4 APU
16.8KWhr LiFePO4, 2.52 kw solar, 10kva Victron split phase
PNW Fireguy is offline   Reply With Quote
Old 05-08-2022, 09:42 PM   #16
firestation12
Montana Fan
 
Join Date: Jul 2019
Location: Mesa
Posts: 277
M.O.C. #24588
For your batteries to charge and discharge equally, be sure the positive and ground cables connect at opposite ends of the 8 battery string.
firestation12 is offline   Reply With Quote
Old 05-09-2022, 08:29 AM   #17
Bruce in DFW
Established Member
 
Join Date: Mar 2021
Location: Allen
Posts: 31
M.O.C. #28272
Sorry, this question is not directly related to the thread, but I've been wondering how people can have so much solar - panels, batteries, inverters, etc. - without exceeding the GVWR of the trailer? We only have 2 x AGM batteries - no solar - and we are at/over the GVWR. I would love to have a similar setup described here - 8x Battleborn - 2000+ solar - but I can't afford the weight. Do you just pack light or have you done axle and suspension upgrades?
Bruce in DFW is offline   Reply With Quote
Old 05-09-2022, 08:58 AM   #18
rames14
Montana Master
 
rames14's Avatar
 
Join Date: Aug 2004
Location: Livermore
Posts: 5,135
M.O.C. #1920
I am not sure what all you are carrying in your unit, and since you didn’t mention year or model, it is difficult to give a full answer. Typically, lithium batteries are about 1/3 the weight of your AGM batteries. A typical solar panel will check in at about 35-40 lbs. Ancillary equipment like SCC’s and Inverters will add another 40 lbs or so. I am probably lighter than my 4 6 volt golf cart batteries in the last rig. We did upgrade our suspension to IS, but matching the 7000 lb axles that came on our unit.
__________________
Ron and Terrie Ames - MOC #1920/KF0NTA
2021Montana 3230CK Super Solar Legacy Package
2021 Ram 3500 Laramie Longhorn, BIM Charging
4x4, SRW, LB, Crew Cab, Pullrite 3900 Hitch
rames14 is offline   Reply With Quote
Old 05-09-2022, 09:56 AM   #19
Bruce in DFW
Established Member
 
Join Date: Mar 2021
Location: Allen
Posts: 31
M.O.C. #28272
We have a 2017 Montana 3811MS with a GVWR around 16,800. We are definitely packing too much and too heavy. The last time I weighed it, we were just over 17K loaded. We were on the road for 4+ months last summer and 5+ the summer before. So, we had portable generators, tools and lots of "just in case" type of items. I'll have to do a better job of packing lighter - and try to convince my wife to do the same.
__________________
2019 F350 LB CC 4x4 6.7L PowerStroke
2017 Montana 3811MS
2019 Rad Rover and Rad Mini Step-Thru
Bruce in DFW is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 02:05 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.