Slides and Level Up not working, Hot red wire tripping 50amp auto breaker
2016 Montana 3950BR.
Hoping you guys can help, had issue this weekend where Level Up and Slides would not work (no power to Level Up Panel), could hear 50 amp breaker clicking/resetting. Replaced breaker and still slides and Level up would not work. Did find while replacing breaker that there was a red wire coming from the breaker that was warm/hot. I disconnected that wire, breaker quit tripping and everything started working as normal. Problem is (or maybe not a problem...lol), I don't know what that red wire goes to (it goes underneath belly), but I checked everything I could think of and seems to be working. Any ideas?
|
|
|
11-14-2022, 06:33 AM
|
#2
|
Montana Master
Join Date: May 2019
Location: Alton
Posts: 2,654
M.O.C. #24086
|
If it is a 10 gauge red wire, it may go to your tank heaters?
__________________
Daryl and Marianne,
2019 3130re 20th Anniversary Edition
2016 F350 Lariat
|
|
|
11-14-2022, 06:57 AM
|
#3
|
Established Member
Join Date: Jul 2017
Location: Boones Mill
Posts: 47
M.O.C. #20124
|
Quote:
Originally Posted by Daryles
If it is a 10 gauge red wire, it may go to your tank heaters?
|
.
Would lights for tank heaters still come on in control panel if it was for the tank heaters?
|
|
|
11-14-2022, 08:24 AM
|
#4
|
Montana Master
Join Date: May 2019
Location: Alton
Posts: 2,654
M.O.C. #24086
|
Quote:
Originally Posted by fre1fred2
.
Would lights for tank heaters still come on in control panel if it was for the tank heaters?
|
Yes, the lights come on when the switch is on.
The switch controls a relay
https://www.montanaowners.com/forums/showthread.php?t=83900&highlight=Tank+heaters
See post #7.
|
|
|
11-30-2022, 04:46 PM
|
#5
|
New Member
Join Date: Jan 2019
Location: Kalama
Posts: 6
M.O.C. #23346
|
One time when we had a similar problem that I spent an entire day chasing, it turned out to be that we coiled up the pigtail and stuffed it in the pin box and as luck would have it, the red / hot wire inside of the pigtail plug landed straight down on a screw causing a dead short! Those screws no longer protrude into the pin box.
|
|
|
11-30-2022, 06:22 PM
|
#6
|
Montana Master
Join Date: Jun 2020
Location: Qualicum Beach
Posts: 665
M.O.C. #26399
|
Quote:
Originally Posted by fre1fred2
2016 Montana 3950BR.
Hoping you guys can help, had issue this weekend where Level Up and Slides would not work (no power to Level Up Panel), could hear 50 amp breaker clicking/resetting. Replaced breaker and still slides and Level up would not work. Did find while replacing breaker that there was a red wire coming from the breaker that was warm/hot. I disconnected that wire, breaker quit tripping and everything started working as normal. Problem is (or maybe not a problem...lol), I don't know what that red wire goes to (it goes underneath belly), but I checked everything I could think of and seems to be working. Any ideas?
|
Lippert issued a directive to up the breaker to 80 amps.
__________________
2018 Keystone Montana 3811MS
2017 Ford F450 diesel dually
600AH Battle Born Lithium Batteries, 1,080 watts solar
3,000 watt hybrid inverter with 120A charger
|
|
|
12-06-2022, 07:53 PM
|
#7
|
Montana Master
Join Date: Jan 2016
Location: STAYTON
Posts: 1,118
M.O.C. #18157
|
This.. The 80A breakers are available on Amazon. Your problem will disappear!
__________________
“Hard times create strong men, strong men create good times, good times create weak men, and weak men create hard times.”
|
|
|
12-06-2022, 08:09 PM
|
#8
|
Montana Master
Join Date: Oct 2012
Location: Box Elder
Posts: 4,676
M.O.C. #12947
|
The original breaker that provides power to the hydraulic pump motor also usually has an additional wire attached that feeds the 12 volt side of the inside panel and this is where power from the converter comes through that charges the batteries. This circuit goes through the battery disconnect switch. When you replace the 50 amp breaker with an 80 amp breaker, connect the battery cable to the battery terminal of the new breaker and the two cables that are connected to the load terminal to the same terminal on the new breaker. You will need to make the holes in the ring terminals a bit larger to fit the larger terminal posts on the 80 amp breaker.
__________________
Bob & Becky
2012 3402RL
2012 Chevy 2500HD D/A CC 4WD
|
|
|
12-08-2022, 11:27 AM
|
#9
|
Montana Fan
Join Date: Apr 2021
Location: everywhere, USA
Posts: 276
M.O.C. #28634
|
2021 3761fl
Ours came from the factory with an 80 amp breaker. Lucky me, I didn't have to change it. When it's cold the Lippert levelers really are working hard to do their job! And remember lower voltage causes higher amperage, that is why Lippert suggests running levelers and slides while on shore power. That way the converter can help out.
__________________
2021 Montana 3761FL, 9 LIFPO4 batteries & 1700 watts of panels w/ Multiplus II 3K inverter and 30amp DC to DC charger from truck. 8k Dexter axles w/ Kodiak disc brakes.
2019 6.7 diesel F350 DRW with Banks derringer and 4"exhaust, airlift bags, 25k B & W Companion hitch, 45 gal. aux. diesel tank and 14k Winch, just in case!
|
|
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Threads |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|