Using Honda 2200 with 3791RD Help

Help I am new to running the generator with a Montana RV so today we lost electricity then I went out started my Honda generator unplugged the Rv 50 amp cable from the post put a dog bone on it to plug it in to the 30 amp connection on the generator. I assume that the RV would run off of the generator with one air conditioner some miscellaneous other items but nothing happened. I then took a small white lamp outside and plugged it into the 20amp reciprocal on the generator and it worked fine. What else do I need to do as far as prep work to get the generator to run my RV?

Thanks for the help
Larry
 
Lhinkle114 is offline   Reply With Quote
Old 07-19-2022, 05:42 PM   #2
Daryles
Montana Master
 
Daryles's Avatar
 
Join Date: May 2019
Location: Alton
Posts: 2,680
M.O.C. #24086
Generators have a floating ground.
IF, you have an EMS, it will not allow power through.
If you can disconnect your EMS and plug your 30A dogbone directly into the Generator it will work fine.
IF you cannot bypass the EMS, you will need a bonding plug to plug into any regular receptacle on the Generator.
The bonding plug bonds the neutral and ground together like your house is wired.

Reference
https://www.rvtravel.com/rv-electric...nding-bonding/

https://www.rvtravel.com/?s=Bonding+plug+

https://www.rvtravel.com/rv-electric...nding-rvt-976/

https://www.rvtravel.com/rv-electric...onding-basics/
__________________
Daryl and Marianne,
2019 3130re 20th Anniversary Edition
2016 F350 Lariat
Daryles is offline   Reply With Quote
Old 07-19-2022, 06:08 PM   #3
Lhinkle114
Montana Fan
 
Join Date: Dec 2019
Location: Rockford
Posts: 147
M.O.C. #25520
Thanks you for the help, I forgot to mention that I did put a grounding plug in my 20amp outlet of a generator but I also forgot to mention that I do have a inline bulldog surge protector and inline Hughes Autoformer. Is there anything else I can do?
Lhinkle114 is offline   Reply With Quote
Old 07-19-2022, 08:23 PM   #4
dieselguy
Montana Master
 
dieselguy's Avatar
 
Join Date: Feb 2005
Location: Haysville
Posts: 4,261
M.O.C. #3085
We have had an Autoformer for years ... our Kipor generator flat doesn't like it, so we've always had to take it out of play while using a generator. You'll not have much luck trying to run an A/C off a 2200 watt generator in super hot weather even with everything else shut off. Try plugging the generator in direct to your fiver via the dogbone ... it won't hurt anything.
dieselguy is offline   Reply With Quote
Old 07-19-2022, 08:38 PM   #5
Carl n Susan
Site Team
 
Carl n Susan's Avatar
 
Join Date: Oct 2005
Location: Carmichael - CA
Posts: 7,359
M.O.C. #4831
Is it possible that the 30 amp plug is not operative on a Honda 2200i *IF* a parallel Honda 2200i is not connected? I don't have one those models and don't know how it works.
As others have written, a Honda 2200i will have a hard time running an AC if you don't have SoftStarts and anything else turned on (like the converter).
__________________
Carl (n Susan)
There is more to life than fuel mileage.
2012 Montana 3700RL Big Sky Package towed by a 2015 Ford F350 6.7L PSD 4WD CC LWB

Carl n Susan is offline   Reply With Quote
Old 07-19-2022, 08:41 PM   #6
Daryles
Montana Master
 
Daryles's Avatar
 
Join Date: May 2019
Location: Alton
Posts: 2,680
M.O.C. #24086
Quote:
Originally Posted by Lhinkle114 View Post
Thanks you for the help, I forgot to mention that I did put a grounding plug in my 20amp outlet of a generator but I also forgot to mention that I do have a inline bulldog surge protector and inline Hughes Autoformer. Is there anything else I can do?
Those references is all I have. You may need to bypass your EMS.
Daryles is offline   Reply With Quote
Old 07-19-2022, 08:52 PM   #7
Jermba623
New Member
 
Join Date: Jul 2022
Location: Fredericktown
Posts: 5
M.O.C. #31343
With a 2200 a soft start will help a bunch. I use a 3500 for mine it will run the whole rig nicely if I have the fridge and water heater on gas, thats without a soft start though. If I had one I could probably run the fridge on electric too. Check to make sure the breaker on the 30 amp plug isn't popped for some reason.
Jermba623 is offline   Reply With Quote
Old 07-19-2022, 09:07 PM   #8
rohrmann
Montana Master
 
rohrmann's Avatar
 
Join Date: Oct 2012
Location: Box Elder
Posts: 4,692
M.O.C. #12947
A 2200 Honda by itself will not work for what you want. We have been about a month here in Nevada running our pair of Honda's, 2000 models, one the Companion, the other the regular one, banked together. We don't have a residential fridge, but the RV fridge is on gas only as is the water heater. Only one A/C at a time, and if the microwave is needed, the A/C gets turned off. Fortunately it cools off enough at night that we can turn off one and put the other into the ECO mode. We have the Progressive hard wired EMS and the grounding plug works fine. I have a six gallon boat tank with the fittings and gas caps that feed both generators so they don't run out of gas. https://www.amazon.com/Bergs-System-.../dp/B003BURT3C
Attached Thumbnails
Click image for larger version

Name:	RV generator setup.jpg
Views:	38
Size:	316.7 KB
ID:	12545  
__________________
Bob & Becky
2012 3402RL
2012 Chevy 2500HD D/A CC 4WD
rohrmann is offline   Reply With Quote
Old 07-20-2022, 05:56 AM   #9
Daryles
Montana Master
 
Daryles's Avatar
 
Join Date: May 2019
Location: Alton
Posts: 2,680
M.O.C. #24086
I would check with
Mike Sokol of
RVELECTRICITY FB group
https://www.facebook.com/groups/rvel...ity/?ref=share

He writes those electrical articles for RV Travel.
Many very knowledgeable people there.
They have been known to call people and walk them through troubleshooting their electrical problems.
__________________
Daryl and Marianne,
2019 3130re 20th Anniversary Edition
2016 F350 Lariat
Daryles is offline   Reply With Quote
Old 07-20-2022, 08:58 PM   #10
Lhinkle114
Montana Fan
 
Join Date: Dec 2019
Location: Rockford
Posts: 147
M.O.C. #25520
Do you need a bonding plug for both generators when running in parallel?
Lhinkle114 is offline   Reply With Quote
Old 07-21-2022, 07:20 AM   #11
Daryles
Montana Master
 
Daryles's Avatar
 
Join Date: May 2019
Location: Alton
Posts: 2,680
M.O.C. #24086
Quote:
Originally Posted by Lhinkle114 View Post
Do you need a bonding plug for both generators when running in parallel?

Here you go

https://www.rvtravel.com/rv-electricity-companion-bonding-plug/
Daryles is offline   Reply With Quote
Old 07-21-2022, 06:18 PM   #12
rohrmann
Montana Master
 
rohrmann's Avatar
 
Join Date: Oct 2012
Location: Box Elder
Posts: 4,692
M.O.C. #12947
Quote:
Originally Posted by Lhinkle114 View Post
Do you need a bonding plug for both generators when running in parallel?

No, one bonding plug is all that's needed. I use it on the companion generator, and when we don't need both running, just turn off the other genny and all is good from the companion one. And, the 30 amp outlet is always hot regardless of using just the one or with them in parallel.
__________________
Bob & Becky
2012 3402RL
2012 Chevy 2500HD D/A CC 4WD
rohrmann is offline   Reply With Quote
Old 07-21-2022, 06:50 PM   #13
Lhinkle114
Montana Fan
 
Join Date: Dec 2019
Location: Rockford
Posts: 147
M.O.C. #25520
Thank you to everyone who helped me. I was able to run the generator with the RV. But the sequence when hooking up is my mistake. The bonding plug must go in first then wait for generator to warm before hooking rv. But I did learn that I need a second generator to run the 15000 air.
Lhinkle114 is offline   Reply With Quote
Old 07-22-2022, 09:23 PM   #14
h2ojocky
Montana Master
 
Join Date: Nov 2012
Location: Rancho Santa Margarita
Posts: 633
M.O.C. #13025
I have a 15K A/C with a soft start and a Honda 2000. i can run my air conditioner if i turn off all other power draws.
__________________
Russ and Linda, So. California
2004 Chevy Silverado 2500 HD, D/A, SRW, SB
2005 2955RL, Pullrite Superglide 16K hitch. Bridgestone Duravis R500 tires. EZ Flex Equilizers with wet bolts.EMS HW50C, Disk brakes
h2ojocky is offline   Reply With Quote
Old 07-24-2022, 03:32 PM   #15
Dan50
Established Member
 
Join Date: Nov 2004
Location: Brossard
Posts: 18
M.O.C. #2474
Quote:
Originally Posted by Lhinkle114 View Post
Help I am new to running the generator with a Montana RV so today we lost electricity then I went out started my Honda generator unplugged the Rv 50 amp cable from the post put a dog bone on it to plug it in to the 30 amp connection on the generator. I assume that the RV would run off of the generator with one air conditioner some miscellaneous other items but nothing happened. I then took a small white lamp outside and plugged it into the 20amp reciprocal on the generator and it worked fine. What else do I need to do as far as prep work to get the generator to run my RV?

Thanks for the help
Larry
This allows me to run a 15,000 BTU A/C with my Yamaha 2400.
https://www.microair.net/collections...r-conditioners
Dan50 is offline   Reply With Quote
Old 07-24-2022, 04:28 PM   #16
dieselguy
Montana Master
 
dieselguy's Avatar
 
Join Date: Feb 2005
Location: Haysville
Posts: 4,261
M.O.C. #3085
For the benefit of all, I think it needs to be clarified that a soft start does not reduced the running amps of the air conditioner just the startup amp draw. A typical 15K AC draws between 12 and 14 running amps especially in this latest heat wave. At least this has been my experience.
dieselguy is offline   Reply With Quote
Old 07-24-2022, 06:09 PM   #17
mlh
Montana Master
 
Join Date: Oct 2004
Location: Salem
Posts: 7,548
M.O.C. #2283
Your generator should put out 1800 running watts. It has 2200 starting watts. My 15000 AC pulls about 1500 watts so your generator should run it without almost nothing else on. You will need a soft start to get the AC running. My 2000 watt Predator has 1600 running watts and will run my 15000 AC at least for a short period of time. I don’t know how long it will run the AC, never tried it.
Lynwood
__________________
www.harrellsprec.com
Lynwood Harrell
323 RL HC 2008 F250
mlh is offline   Reply With Quote
Old 07-26-2022, 11:21 AM   #18
Randy E
Montana Fan
 
Join Date: Apr 2018
Location: Hermitage
Posts: 138
M.O.C. #21626
We have a 2017 3791RD also. We can run 1 AC unit using our Honda EU2200i generator as long as we turn off everything else. We use a bonding plug as well. 1 AC unit pulls 14 amps while running. Get a good soft start on both ac units. Micro-Air has great soft starters and thermostats for both units. Highly recommend both.
Attached Thumbnails
Click image for larger version

Name:	IMG_0001.jpg
Views:	20
Size:	130.4 KB
ID:	12597  
__________________
Randy & Tracy Elsey
Hermitage Pa.
2017 3791RD
2016 Chevy DD 4x4
Randy E is offline   Reply With Quote
Old 07-26-2022, 01:18 PM   #19
twindman
Montana Master
 
twindman's Avatar
 
Join Date: Apr 2006
Location: Mesa az
Posts: 2,945
M.O.C. #5651
Another thing to look out for - the converter pulls several amps if the batteries are at all down a bit. So even with nothing else on, you could be too high amps with the A/C running. Unless you just pop the breaker on the converter.
__________________

Tom and Gail
2013 Mountaineer 362
2012 Silverado 2500
twindman is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 05:13 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.