Electrical question-30 amp power plus generator

We are moving our 3791 to a campground that has 30amp power. They have some spots for 50 amp but long waiting list to get on those. My question is if you dogbone a 30amp shore power plus a 30 amp generator connection to 50amp plug. Will this work to provide two 30amp legs to each side of the camper. My thoughts were on days when very hot to use a invertor generator to power the Air Conditioner on the 2nd leg.
 
__________________
2015 Mountainneer 350qbq
2016 Ram 3500 DRW
2020 Ford F350
2019 Montana 3791RD
ncrzrbk is offline   Reply With Quote
Old 11-03-2021, 08:07 AM   #2
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,133
M.O.C. #6433
I would not do that. 50 amp service has two hot legs 180 degrees out of phase and uses a common neutral for the two hot legs. Using a 30 amp service and a generator would be two hot legs with unknown phase difference and two separate neutrals connected to a common neutral for the trailer. I really don't know what the end result might be, but I think the neutral would be trying to carry an unnatural neutral flow. I would not try it.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 11-03-2021, 08:48 AM   #3
NCFischers
Montana Master
 
Join Date: Aug 2008
Location: New Bern
Posts: 4,369
M.O.C. #8728
Send a message via Yahoo to NCFischers
Do NOT do it!!! You can cause a lot of damage to the RV including a possible fire. Two separate power sources is a recipe for trouble.
NCFischers is offline   Reply With Quote
Old 11-03-2021, 09:23 AM   #4
ncrzrbk
Established Member
 
ncrzrbk's Avatar
 
Join Date: Apr 2015
Location: Kernersville
Posts: 30
M.O.C. #17265
Thank you. And this why I ask. I had not considered the two neutral’s in conflict from the shore power and the generator. I do appreciate the advice.
__________________
2015 Mountainneer 350qbq
2016 Ram 3500 DRW
2020 Ford F350
2019 Montana 3791RD
ncrzrbk is offline   Reply With Quote
Old 11-03-2021, 09:24 AM   #5
ncrzrbk
Established Member
 
ncrzrbk's Avatar
 
Join Date: Apr 2015
Location: Kernersville
Posts: 30
M.O.C. #17265
Thank you both
__________________
2015 Mountainneer 350qbq
2016 Ram 3500 DRW
2020 Ford F350
2019 Montana 3791RD
ncrzrbk is offline   Reply With Quote
Old 11-03-2021, 03:10 PM   #6
Daryles
Montana Master
 
Daryles's Avatar
 
Join Date: May 2019
Location: Alton
Posts: 2,654
M.O.C. #24086
Quote:
Originally Posted by bb_tx View Post
i would not do that. 50 amp service has two hot legs 180 degrees out of phase and uses a common neutral for the two hot legs. Using a 30 amp service and a generator would be two hot legs with unknown phase difference and two separate neutrals connected to a common neutral for the trailer. I really don't know what the end result might be, but i think the neutral would be trying to carry an unnatural neutral flow. I would not try it.

good advice 👍
Daryles is offline   Reply With Quote
Old 11-03-2021, 03:49 PM   #7
jimcol
Montana Master
 
jimcol's Avatar
 
Join Date: Dec 2007
Location: Kansas City, Missouri
Posts: 2,702
M.O.C. #7992
Send a message via AIM to jimcol Send a message via MSN to jimcol
Good advice from the respondents to not do what you are proposing. You can, however, take the wire feeding the second air conditioner off the buss and feed it with the generator. Know several people on this forum who have connected the wire to a heavy duty extension cord and ran it to another outlet in the park power pedestal. (Some called it a cheater plug. Some parks frowned on it.)Instead of running it to the pedestal just run it to your generator.
__________________
2006 3000RK
2009 Ram 2500
jimcol is offline   Reply With Quote
Old 11-17-2021, 01:44 PM   #8
bcrvman
Montana Master
 
Join Date: Jun 2020
Location: Qualicum Beach
Posts: 665
M.O.C. #26399
Quote:
Originally Posted by ncrzrbk View Post
We are moving our 3791 to a campground that has 30amp power. They have some spots for 50 amp but long waiting list to get on those. My question is if you dogbone a 30amp shore power plus a 30 amp generator connection to 50amp plug. Will this work to provide two 30amp legs to each side of the camper. My thoughts were on days when very hot to use a invertor generator to power the Air Conditioner on the 2nd leg.
ELECTRICIAN here. NO, do not attempt.
I can do something similar, but you may feel it is too expensive.
My setup: shore power is standard 30A with an additional 20A from my inverter. That requires a 3,000W Victron Inverter and a correctly sized battery bank. I would not try it with Lead Acid, only Lithium. If you NEVER boondock, then a single Battle Born or Lion will do, but if you do boondock even once, then 4 to 6 depending on your energy requirements (audit). You will also need a Victron battery monmitor, a GX device of some sort, BIG welder cables for the 200A battery draw plus misc marine grade connectors, bus bars etc etc. Altogether several thousand dollars. OR go someplace cooler.
__________________
2018 Keystone Montana 3811MS
2017 Ford F450 diesel dually
600AH Battle Born Lithium Batteries, 1,080 watts solar
3,000 watt hybrid inverter with 120A charger
bcrvman is offline   Reply With Quote
Old 11-17-2021, 03:47 PM   #9
firestation12
Montana Fan
 
Join Date: Jul 2019
Location: Mesa
Posts: 277
M.O.C. #24588
I'll let what others have commented be the final word. I'll suggest that you can improve your power management of the available 30 amps, by installing a soft start on A/C units. Also use an EMS's display or amp meter to choose which items such as refrigerator, voltage converter, water heater....etc, to determine how many items can run on the 30 amp shore power, leaving the rest run on propane. Don't forget to consider the intermittent amperage spike of the microwave oven.
firestation12 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 12:53 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.