Old 05-24-2022, 12:29 PM   #1
Guy from Cowtown
New Member
 
Join Date: May 2021
Location: Calgary
Posts: 6
M.O.C. #28812
Furnace cycling off and on frequently

Hi everyone. We are a 2020 3120RL. Our furnace has started cycling on and off frequently, i.e. kicks in, runs 10 seconds then cuts off for 10 seconds, on 10-off-10, and just keeps repeating until it reaches the desired inside temperature (at least we're warm) but its annoying as heck at night. I think I might have replace some kind of heat/ temp sensor or board? Anyone else ever have the same problem? Thanks in advance!!
 
Guy from Cowtown is offline   Reply With Quote
Old 05-24-2022, 02:25 PM   #2
Bourbon County
Montana Fan
 
Join Date: Feb 2022
Location: Cynthiana
Posts: 198
M.O.C. #30449
Most of the furnaces have 2 different fans in them. One is a draft induction blower that supplies air for combustion, this is the first thing you hear when the furnace gets a heat call. There is an air flow sensor for this blower to prove you have combustion air; these are a pretty common failure point and fairly easy to replace. If the furnace is actually lighting the burner, this is not your problem; the burner won't attempt to light without proof of air flow. There is a timer that will time out if you don't get air flow confirmation.

If the burner is lighting and then cycling off pretty quickly, it could well be a flame sensor. The mother board is another possibility, but I wouldn't think likely if it starts the ignition cycle and the main blower comes on. The other fan is the blower that actually circulates the warm air.
Bourbon County is offline   Reply With Quote
Old 05-24-2022, 04:12 PM   #3
jsb5717
Montana Master
 
jsb5717's Avatar
 
Join Date: Mar 2019
Location: Milwaukie, OR
Posts: 1,467
M.O.C. #23668
Could be a few different things. Could be the air flow sensor as stated above. It could also be your propane regulator. Ours was acting similarly until I replaced our OEM Fairview regulator with a Marshal Excelsior regulator. Less likely, it could be your thermostat. If it's a Dometic they can be finicky.

The fact that it's actually completing all of it's pre-ignition functions and firing before shutting down would point me toward the regulator
__________________
Jeff & Sandi (and Teddy - 7lb Schnorkie)
2018 Montana HC 305RL / HW Progressive EMS
2015 RAM 3500 Laramie Longhorn Crew Cab 4x4 DRW / Demco Recon Hitch on RAM Puck Ball
jsb5717 is offline   Reply With Quote
Old 05-24-2022, 04:35 PM   #4
Carl n Susan
Site Team
 
Carl n Susan's Avatar
 
Join Date: Oct 2005
Location: Carmichael - CA
Posts: 7,356
M.O.C. #4831
Not having a newer furnace and not knowing exactly when this came about, but there have been numerous reports that the cheap, poorly made, inferior, 15 amp self-resetting fuse for the furnace may cause this problem. Change to a standard blade fuse and the problem goes away?
__________________
Carl (n Susan)
There is more to life than fuel mileage.
2012 Montana 3700RL Big Sky Package towed by a 2015 Ford F350 6.7L PSD 4WD CC LWB

Carl n Susan is offline   Reply With Quote
Old 05-25-2022, 09:09 AM   #5
Bourbon County
Montana Fan
 
Join Date: Feb 2022
Location: Cynthiana
Posts: 198
M.O.C. #30449
A quick easy check you could do is remove the exterior access cover and check for obstructions in the supply and exhaust. These areas are subject to obstruction by insect nests, leaves, and even sometimes small birds. This is the air path for combustion air and if they are restricted, I doubt you would get the airflow switch to make and the burner would ever fire.

Have you actually measured the 10 second intervals you mentioned, or is that just a guess? When the circulation blower comes on do you hear any unusual noises like a squealing sound? They use sleeve bearings in those motors and they tend to get pretty loud when they fail. A blower motor bearing failing might be enough to overload and drop out.
Bourbon County is offline   Reply With Quote
Old 05-25-2022, 02:33 PM   #6
steiny93
Montana Fan
 
Join Date: May 2015
Location: fargo
Posts: 185
M.O.C. #17461
could be tripping from the 'high limit switch'

When it cycles, does the fan continue to run but the burner is cycling? Or are you saying that the fan in cycling (stopping and restarting)?

If the fan runs continuously but the burner is cycling it could be that the switch is bad or you have an obstruction in the air way.

I'd recommend starting by verifying that all the ducts are opened and not restricted, it's common to have an air restriction cause this type of behavior, very common with fish houses.
steiny93 is offline   Reply With Quote
Old 05-25-2022, 03:40 PM   #7
Arkware
Montana Master
 
Join Date: Aug 2015
Location: Mena
Posts: 504
M.O.C. #17723
I second Carl's suggestion. The 12 volt re-setable fuse.
Had trouble with mine and replaced the fuse with a 'standard' fuse.
no trouble since.
__________________
Ron & Rhonda
2021 3230CK Montana Legacy w/ Super SolarFlex
(old rig) 2015 Montana 3611RL 8K I.S., Disk Brakes, Sailun Tires
2015 F350 XLT Crew Dually 20K B&W Companion
Arkware is offline   Reply With Quote
Old 05-26-2022, 06:53 AM   #8
Wisconsin Retiree
Montana Fan
 
Wisconsin Retiree's Avatar
 
Join Date: Jan 2021
Location: Coloma, Wisconsin
Posts: 202
M.O.C. #28036
Not to change the subject but out of curiosity how loud are your furnaces? Aside from very noisy inside the trailer when I am outside my furnace sounds extremely loud to me? The guy next site even commented how it sounds like an industrial size furnace??? Are others as loud?
__________________
Chuck
2019 3121RL 35 ft., 2020 3500 Dodge Ram SRW, Cummins 6.7 HO, Air Bags - Air Lift BT Wireless Compressor, Coloma, Wisconsin
Wisconsin Retiree is offline   Reply With Quote
Old 05-26-2022, 08:06 AM   #9
jsb5717
Montana Master
 
jsb5717's Avatar
 
Join Date: Mar 2019
Location: Milwaukie, OR
Posts: 1,467
M.O.C. #23668
Quote:
Originally Posted by Wisconsin Retiree View Post
Not to change the subject but out of curiosity how loud are your furnaces? Aside from very noisy inside the trailer when I am outside my furnace sounds extremely loud to me? The guy next site even commented how it sounds like an industrial size furnace??? Are others as loud?
They're all loud. Some have said that the Suburbans might be a little quieter than the Atwoods but they are still loud. There are also different BTU furnace sizes, which will likely have show variable in volume. Ours is surprisingly quiet indoors, but that's due to placement and insulation between the furnace and living space. Outdoors ours still sounds like a blast furnace.
__________________
Jeff & Sandi (and Teddy - 7lb Schnorkie)
2018 Montana HC 305RL / HW Progressive EMS
2015 RAM 3500 Laramie Longhorn Crew Cab 4x4 DRW / Demco Recon Hitch on RAM Puck Ball
jsb5717 is offline   Reply With Quote
Old 05-29-2022, 03:48 PM   #10
Denali
New Member
 
Join Date: Feb 2022
Location: Warsaw
Posts: 6
M.O.C. #30527
Sometimes it’s because the furnace is not getting gas. Turn on your gas stove and your gas hot water heater. Let them run and then try out your furnace. Also check your battery as the furnace get 12 volt power to operate. I try little things first
Denali is offline   Reply With Quote
Old 05-29-2022, 09:04 PM   #11
DaveK
Montana Fan
 
Join Date: Feb 2019
Location: Fredericksburg
Posts: 163
M.O.C. #23470
We had the re-setting fuse problem as well.

We also had the control board replaced under warranty.
DaveK is offline   Reply With Quote
Old 05-30-2022, 09:30 AM   #12
nellie1289
Seasoned Camper
 
Join Date: Feb 2021
Location: Portland
Posts: 68
M.O.C. #28145
This is a timely post for me as well. We are out in our 2021 this weekend and i seem to be having similar issues. We have never really used our furnace before as we only go out in summer but it has been chilly here in the northwest. i do check the furnace exahust for pets and run it once in a while to make sure there is no issues. I put the thermostat to "heat/Electric" and the gas furnace definitely fires. You hear a fan kick on, then the furnace fire, then it blows heat for about 1 minute. The heat pump seems to turn on too. Then about a minute later it turns both off, and then both come back on and the process continues as the temperature slowly comes up. I have no idea what is wrong.

Also how come my thermostat sometimes shows "heat-gas" "heat gas-electric" and some times "heat-Electric". What im saying is sometimes "heat-electric" is not one of the toggle options.

I have the coleman airxcel thermostat and heat/pump air conditioners
__________________

2021 Montana 3854BR with 2014 Ram 3500 SRW Limited CC LB, 2021 Malibu 23 LSV, 2019 Can AM XRS turbo, 2017 Yamaha YXZ 1000R
nellie1289 is offline   Reply With Quote
Old 07-30-2022, 10:42 AM   #13
MOODY
Seasoned Camper
 
MOODY's Avatar
 
Join Date: Sep 2019
Location: Rattan
Posts: 67
M.O.C. #24936
2020 Montana - furnace would come on & after 5-10 seconds the furnace would go out. The fan would continuously run. After 5-10 seconds the furnace would relight and after 5-10 seconds the furnace would go out again. This process would continue for 10-15 minutes before it would time out. Replaced to many parts to describe.
Finally found a memo that stated at point of installion that the furnace was carried by the propane line as a handle and slightly bent the line. Advised to push the line back and to the right slightly- 1/4 - 1/2 inch. Also read about oil in the propane lines.
Repositioned the fuel line. Disconnected the propane line at the bottom of the trailer where the flex line from the regulator attaches to steel pipe and at the furnace inlet. Blew out the line with compressed air at 100 psi. Did not notice any oil or debris.
Furnace works fantastic now. I have been having this problem for over a year. It used to work only with temps above 35 degrees but in the past 6 months has not worked at all.
Installed a drip line at the regulator to take care of any future oil contamination. Search for rv propane line oil contamination and you might be surprised at your findings.
My furnace always acted as if it was starving for fuel. Any repair I would start with blowing out the lines & then progress from there.
__________________

Kevin & Pat Moody
2020 Montana 3701LK, Legacy Package, Satellite, Solar, Generator, 2019 Ford F350 Dually, BD5F Trailer Saver, 12' Trailer with Kayak Rack, Polaris General XP 4 1000
MOODY is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 08:32 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.