Installing a 50 amp receptacle off of an existing breaker box at the farm. Already has 50 amp power, but the run is 220 feet.

I've done a receptacle before but it was 10 feet off the box.

What wire would be recommended for such a long run? Aluminum or copper, direct burial or in conduit.

Any help is appreciated.
 
__________________

2020 Montana High Country 377FL
Edge CTSV2 Diesel Tuner
Airlift LoadLifter 5000 bags
rws262 is offline   Reply With Quote
Old 08-30-2021, 09:17 AM   #2
mlh
Montana Master
 
Join Date: Oct 2004
Location: Salem
Posts: 7,552
M.O.C. #2283
I would run copper but it is very expensive right now. I think prices will come down. Aluminum will work. I ran standard wire to my camper over a hundred yards not under ground without conduit over 20 years ago. Just be careful to not get any rocks near it. A crosstie plant near us never uses underground wire with all the extreme use it gets with tractor trailers and big fork trucks that can carry a tractor trailer.
Lynwood
__________________
www.harrellsprec.com
Lynwood Harrell
323 RL HC 2008 F250
mlh is online now   Reply With Quote
Old 08-30-2021, 09:49 AM   #3
Akuhn
Established Member
 
Join Date: Jul 2021
Location: Glenville
Posts: 27
M.O.C. #29184
For that length I would run #2 URD. It's a bear to wire to the outlet in the box, but you shouldnt have any issues with power. I just ran 130 ft for our 5th wheel, went with #2 because they were out of #4.
__________________
2021 MHC 376FL
2022 Ram 3500 Cummins DRW
Akuhn is offline   Reply With Quote
Old 08-30-2021, 10:34 AM   #4
Creeker
Montana Fan
 
Join Date: Nov 2018
Location: Charleston
Posts: 455
M.O.C. #23094
Can you run it overhead in free air?


Aluminum Quadruplex aerial cable can be ran much, much cheaper than copper under ground.
__________________
2019 Montana HC 310RE
2010 Wildcat 29RLBS
2014 Ford F-350 Lariat 6.7
Creeker is offline   Reply With Quote
Old 08-30-2021, 10:39 AM   #5
Akuhn
Established Member
 
Join Date: Jul 2021
Location: Glenville
Posts: 27
M.O.C. #29184
Quote:
Originally Posted by Creeker View Post
Can you run it overhead in free air?


Aluminum Quadruplex aerial cable can be ran much, much cheaper than copper under ground.
Yes you can run it over head. I'm not sure of the price of Ariel cable, the kind I used was aluminum.
Akuhn is offline   Reply With Quote
Old 08-30-2021, 01:39 PM   #6
mlh
Montana Master
 
Join Date: Oct 2004
Location: Salem
Posts: 7,552
M.O.C. #2283
I ran aerial aluminum cable from my home place to a mobile home, or make that a trailer one time. The country said I needed a permit that they wouldn’t give me and I said I didn’t need anything so I ran the cable underground. Worked fine for 10 years until I build my present home 45 years ago.
Never did like someone telling me what I could do. It’s like what do you mean I can’t, I just did it.
Lynwood
__________________
www.harrellsprec.com
Lynwood Harrell
323 RL HC 2008 F250
mlh is online now   Reply With Quote
Old 08-30-2021, 02:10 PM   #7
DadsHemi
Montana Master
 
DadsHemi's Avatar
 
Join Date: Sep 2017
Location: Florence
Posts: 945
M.O.C. #20472
At 220’ you can use #4 copper or #2 Aluminum, I’d go underground PVC conduit. Any longer you would need to upsize the wire.
__________________

2018 Ram 3500 MegaCab 4x4 Aisin, 4:10 Gears
Titan 50 Gal Tank, Air Lift Wireless Bags
2017 3160 RL
DadsHemi is offline   Reply With Quote
Old 08-30-2021, 06:06 PM   #8
5acresofchaos
Established Member
 
Join Date: Aug 2021
Location: Franktown
Posts: 25
M.O.C. #29489
DW always says,”There are rules and there is what my husband does”.
__________________
Daryl and Debbie
Colorado
2021 3855BR Legacy
2019 F350 SRW
5acresofchaos is offline   Reply With Quote
Old 08-30-2021, 08:11 PM   #9
Dam Worker
Montana Master
 
Join Date: Mar 2015
Location: West Richland
Posts: 1,253
M.O.C. #17164
Lots of good information on the WEB. I have just put in a 60amp sub panel using #6 wire with a 90’ run. 110/120 volt requires big wires especially over long distances. I think code say that anything over 100’ you have to upsize the cable. Might have to double that at over 200 feet. Last thing you need is lots of voltage drop. If you do go underground with conduit make sure your wire is rated THWN although my wire came rated THWN and THHN. If you look up the amperage in NEC you can usually find what size conduit, wire size for that distance and also ground cable size etc.
Good luck, be safe and get a permit or even hire an electrician.����

Tom Marty
__________________
Dam Worker is offline   Reply With Quote
Old 08-31-2021, 04:13 AM   #10
Mikendebbie
Montana Master
 
Mikendebbie's Avatar
 
Join Date: Jan 2018
Location: Austin
Posts: 2,424
M.O.C. #21044
My electrician is coming today to get started on 140’ underground of 2” conduit. I think he plans to use #4 aluminum. I am also dropping my overhead primary to underground. It’s only 54’ but it crosses my driveway. The first time I brought the Montana home I discovered I could not safely clear the line. I concreted a temporary pole to prop it up until I could get it changed to underground. Looking forward to taking my temp pole down.
__________________
MikenDebbie Aggie ‘77 in the sticks near Austin TX
2019 Chevy 3500 High Country DRW
2018 Montana 3921FB
Aussie Gus + Texas Heeler Jimmy
Mikendebbie is offline   Reply With Quote
Old 09-01-2021, 08:29 AM   #11
rws262
Established Member
 
Join Date: Sep 2020
Location: Miller County
Posts: 20
M.O.C. #27069
A lot of good replies. When buying copper wire, I've got 6 gauge for the two hots, but is it possible to use smaller wire for the neutral or ground?
__________________

2020 Montana High Country 377FL
Edge CTSV2 Diesel Tuner
Airlift LoadLifter 5000 bags
rws262 is offline   Reply With Quote
Old 09-01-2021, 10:23 AM   #12
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,171
M.O.C. #6433
The neutral should be the same size as the hots. The neutral could possibly carry as little as zero amps (even if the hots are carrying full amps) to as much as the full rated current of one hot (if one hot was pulling max amps and the other hot pulling zero amps). That is a characteristic of split phase 120/240 vac power.

The ground can be smaller but I don’t remember the rule for sizing it.

6 ga is small for that distance. You could have a drop of over 5 volts at 25 amps or over 10 volts at 50 amps according to one voltage drop calculator I looked at.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Old 09-01-2021, 10:47 AM   #13
rws262
Established Member
 
Join Date: Sep 2020
Location: Miller County
Posts: 20
M.O.C. #27069
Quote:
Originally Posted by BB_TX View Post
The neutral should be the same size as the hots. The neutral could possibly carry as little as zero amps (even if the hots are carrying full amps) to as much as the full rated current of one hot (if one hot was pulling max amps and the other hot pulling zero amps). That is a characteristic of split phase 120/240 vac power.

The ground can be smaller but I don’t remember the rule for sizing it.

6 ga is small for that distance. You could have a drop of over 5 volts at 25 amps or over 10 volts at 50 amps according to one voltage drop calculator I looked at.
Thanks for the response! I should have clarified that my run got a lot shorter and is now under 100'.
__________________

2020 Montana High Country 377FL
Edge CTSV2 Diesel Tuner
Airlift LoadLifter 5000 bags
rws262 is offline   Reply With Quote
Old 09-02-2021, 02:52 PM   #14
MARK A
Montana Master
 
Join Date: Jan 2016
Location: STAYTON
Posts: 1,118
M.O.C. #18157
One school of thought..Have enough service for someone to stay over, but not enough to stay LOL


Mark
__________________
“Hard times create strong men, strong men create good times, good times create weak men, and weak men create hard times.”
MARK A is offline   Reply With Quote
Old 09-05-2021, 06:37 PM   #15
Frank64
Montana Fan
 
Join Date: Jun 2019
Location: Summerville
Posts: 138
M.O.C. #24370
50 amp shore power

I checked with the electrical codes for my county and it said I needed to tun #4 copper in electrical pvc underground. This was about 25 years ago
Frank64 is offline   Reply With Quote
Old 09-05-2021, 09:45 PM   #16
GeoMar
New Member
 
Join Date: May 2020
Location: Des Moines
Posts: 6
M.O.C. #26282
I checked the current NEC and you will need a minimum of 3 conductors, #8 THHN (#6 THHW is adequate). The underground conduit is 1.5” PVC schedule 40. The ground size is #10. I recommend installing an outdoor unfused disconnect ahead and next to the outlet (because of the distance from the panel breaker, an inexpensive plastic HVAC type will do).
__________________
2017 Ram DRW, Pullrite Auto Slider, 2019 3120RL Monty
GeoMar is offline   Reply With Quote
Old 09-06-2021, 03:53 AM   #17
Badd857
Established Member
 
Join Date: Nov 2020
Location: Horseshoe Bend
Posts: 19
M.O.C. #27505
Hire a licensed electrician. 😳
Badd857 is offline   Reply With Quote
Old 09-06-2021, 07:29 AM   #18
pitman44
Seasoned Camper
 
Join Date: Dec 2019
Location: Dryden
Posts: 93
M.O.C. #25471
I would run 3 wire to the pedestal and set ground rods at the pedestal for the ground. It may be less expensive and it is permissible to do so.
pitman44 is offline   Reply With Quote
Old 09-06-2021, 08:02 AM   #19
mhs4771
Montana Master
 
mhs4771's Avatar
 
Join Date: Dec 2009
Location: Sebring
Posts: 3,659
M.O.C. #9969
That's how I did mine, three wires from the breaker panel inside to my outside post and installed ground rods around the post. Because it was cheaper, I installed a breaker just before the 50 amp socket.
__________________
Michelle & Ann
2018 Chevy 3500HD High Country DRW 4X4 Crew Cab w/Duramax/Allison, Formally 2010 Montana 2955RL, Now Loaded 2016 SOB, Mor/ryde IS, Disc Brakes & Pin Box, Comfort Ride Hitch, Sailun 17.5 Tires.
mhs4771 is offline   Reply With Quote
Old 09-06-2021, 08:16 AM   #20
BB_TX
Montana Master
 
Join Date: Oct 2006
Location: McKinney
Posts: 7,171
M.O.C. #6433
Quote:
Originally Posted by pitman44 View Post
I would run 3 wire to the pedestal and set ground rods at the pedestal for the ground. It may be less expensive and it is permissible to do so.
I recently had a detached garage/shop building built and that is how the electrician ran the new wiring to it. Required a city permit and inspections so I could not do it myself.
__________________
Bill & Patricia
Riley, our Golden
2007 3075RL (recently sold, currently without)
BB_TX is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Montana RV, Keystone RV Company or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 10:46 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.